Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Residual Current Devise (RCD)

Status
Not open for further replies.

salem

Electrical
Joined
May 2, 2001
Messages
38
Location
AE
0n 415 V TT earthed system, Can we use Residual Current Device (RCD) at load side.

I'm having a case where RCD is tripping when we supply from portable generator with unearthed neutral, but not tripping when we supply from a transformer with earthed neutral.
 
One of your loads may have a capacitive leak that results in an imbalance that would normally be split or resolved via the source's ground which is missing with your generator.

Keith Cress
kcress -
 
The first step will be to ground the generator neutral. If it still trips, check the waveform of the generator output with a scope.
Otherwise as itsmoked suggests or other load related issues.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Question is, do you want to run your system as IT or TT?
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top