Gordonl - one reference is the GEC Measurements Protective Relaying Application Guide, which is an overall great book if you can get your hand on a copy of it. A strong hint is the fact that the minimum setting current on relays such as the SEL501 and the overcurrent elements of the SEL321-1, SEL551 and SEL587 is 0.5A for the 5A model, 0.1A for the 1A model.
Sensitive ground fault relay elements are certainly available, but I believe that they are primarily intended for use with core balance CTs, NOT in the residual circuit of the phase CTs. An example of this is the GE Multilin 750 relay. The manual for this states, relative to sensitive ground elements, that "The sensitive ground current input can be connected to a zero sequence CT for increased sensitivity and accuracy when physically possible in the system." They do show the possibility of a residual connection, but note the comment re sensitivity & accuracy.
I am presently in the process of specifying a high-resistance grounded 2.4 KV system, where I will be using sensitive ground fault elements of the motor protection relays, with core balance CTs, to give an alarm for a ground fault level of 1A primary - I don't think that I could do that reliably with 300/5A phase CTs.