Residential Controls wiring 2

Status
Not open for further replies.

GreenEE

Electrical
Jul 10, 2009
6
Could someone confirm my understanding of how B & O change over lines are supposed to work. I am especially interested in the which power source (RC or RH) supplies B & O

O is powered from RC when cooling is needed (does it mirror Y)
B is powered from RC when heating is needed

Is this correct?

Should G be powered from RC or RH?

Thanks
 
Replies continue below

Recommended for you

The RC terminal is designated for the power for cooling. Some HVAC systems use two transformers. A transformer for cooling and a transformer for heating. In this case the power from the transformer in the air conditioning system would go to the thermostat terminal. It should be noted that a jumper can be installed between RC and RH for a heating and cooling system equipped with a single transformer.
The RH terminal is designated for the power for heating. See RC above for an explanation. It should be noted that a jumper can be installed between RC and RH for a heating and cooling system equipped with a single transformer.
Y – This is the terminal for cooling or air conditioning and goes to the compressor relay. Typically a thermostat wire pull is made to the air handler on split systems and then this wire is spliced for the separate wire pull which is made to the condenser. Some manufacturers put a terminal board strip near the control board in the air handler so a splice is not needed.
W – This is the thermostat terminal for heating. This wire should go directly to the heating source whether it be a gas or oil furnace, electric furnace or boiler.
G – This is the thermostat terminal used for the fan relay to energize the indoor blower fan. On a split system the blower fan is in the air handler while with a package unit the blower fan is in the outdoor package unit.
C – This is the thermostat terminal which originates from the transformer and is necessary to complete the 24 volts power circuit in the thermostat but only if the thermostat consumes electricity for power. Many digital thermostats require 24 volts for power so the common wire is necessary.

O or B – These thermostat terminals are for heat pumps and the B thermostat terminal is used on for Rheem or Ruud and any manufacturer that energizes the reversing valve in heating mode for the heat pump. Most other manufacturers of heat pumps will utilize the reversing valve for cooling and the O thermostat terminal will be utilized for this purpose. This wire goes to outside heat pump condenser where the reversing valve is located.
 