stookeyfpe
Specifier/Regulator
This question is based on the 2007 edition of NFPA 14 but feel free to use the current edition because the requirement hasn't changed.
I have a 32 story high-rise I'm currently reviewing for compliance. The maximum churn pressure for the fire pump is 287 PSIG. The standpipe is constructed using Allied Tube & Conduit Schedule 10 pipe which is listed for pressures to 300 PSIG. It will be assembled using Victaulic Style 005 Firelock grooved couplings which for 6-inch pipe is listed for pressures to 300 PSIG.
NFPA 14 Section 11.4.1 states:
As the AHJ I can require a hydrostatic pressure test of 350 PSIG to the standpipe and fittings based on the referenced section. I would like confirmation if you agree or disagree with my interpretation. I know it's a simple question but I haven't done a high-rise in over a year but in the next 6 months I'll be doing at least 5 standpipe/sprinkler plan reviews on high-rise buildings so I'm asking for guidance.
Thank you.
All new systems, including yard piping and fire department connections, shall be tested hydrostatically at not less than 200 psi (13.8 bar) of pressure for 2 hours, or at 50 psi (3.5 bar) in excess of the maximum pressure where the maximum pressure is in excess of 150 psi (10.3 bar).
Thank you.