First of all, the current has to be measured in A .Second: the panel feed a transformer or a heater delta connected as the panel itself [I cannot imagine how could be] is not delta connected, does it?
Let's say the voltages are equilibrated and equally phased [120 degrees apart].
The total S=15+10+12=37 Kva [apparent power]
Let's say the voltage [L-L] is 400 V then the average current will be=1000*S/sqrt (3)/Voltage=53.4 A
The average Sav=37/3=12.33 kVA and the maximum 15/12.33=1.216
So the maximum may be 53.4*1.216=65 A
This is a conservative solution, but not exaggerated.
If you know the current phasor [vector] angles you may calculate exact the line currents.
According to relation Sum(I) =0 in one corner:
Ia=Iac-Iba ; Ib=Iba-Icb ; Ic=Icb-Iac
If the supplied device is a heater for instance the pf=1 [pure resistance], so the current angle with respect the voltage angle will be 0.
In order to measured the actual angle if pf<1 you need a single-phase wattmeter and the angle with respect the voltage will be = arccosine (P[watts]/S[VA]).
All it remains is plane geometry [in order to calculate one edge when you know the other two and the
angle between in a triangle].
Iab=23.4*1000/400=58.575A [11% less than above approximate calculation.]