Dear Mr. edison123
1. I noticed:
First image-- left palm, no "electrical contact point" around 4 bolting holes,
middle palm, 3 points,
right palm, 3 points.
Second image--top palm, 3 points,
middle palm, 1 point,
bottom palm, 2 points.
Third image--only 1 palm-- top left and right, 2 points,
bottom left, 1 point.
Note: "electrical contact points" are shown by [rough/pitted surface] while the "air gaps" are shown in blue smooth surface.
2. From the above three images, it is evident that [none of them] having good "electrical contact points" around [all four bolting holes]. Possible cause: [uneven tightening torques] between the 4 bolts. Action to be taken: Check that [all four bolts] are tightened [evenly with equal torque].
Check: Bolt size M12 grade 8.8 or higher, nut grade 8 or higher. Use big 28mm or bigger width thickness 2.7mm or thicker washers. In addition, use Belleville washers are highly recommended. Tightening torque 45Nm [evenly for all 4 bolts].
3. Us of electrical inhibitor joint compound is superfluous. Silver-plating or tinning is
unnecessary in normal indoor dry conditions.
4. Opinion: replacing the existing single (100x12) by (2x50x12) bar (may not?) solve the problem. Look into improving the "electrical contact point" area is the essence.
5. Suggestion: File the whole palm area smooth including the pitted and unpitted areas. Using the existing (100x12) bar and take extra attention on the [even tightening torque].
Attention: Make sure to use a calibrated "torque wrench"!.
Che Kuan Yau (Singapore)