If your problem is getting it inspected, Metallic conduit is accepted by NEC, but if the conduit is exposed to the elements I wouldn't recommend it. The joints of the conduit increase in resistance as the conduit deteriorates and in an old installation, the connection to ground may not be sufficient. The NEC suggests using an electrical joint compound as a lubricant to keep the joint impedance low and protect from corrosion. Especially in the case of strong fault, the high resistance will rapidly heat and arc. If this happens where the conduit is buried in concrete, the concrete can explode.
------------------------------------------------------------------------