I have a 200kW 480V Onan generator that has been installed for a few years and the voltage regulator (MX321 AVR) keeps failing (no output). I checked the rotating diodes and all were good, checked all coil resistance and all were good, checked everything for shorts to ground with DMM and all seem ok. There is an isolation transformer board to supply a voltage signal to the AVR and I did find a bad solder joint (this has been fixed) on a prior inspection when the first AVR failed. The generator is connected with an open transition automatic transfer switch and solidly grounded neutral supplying lighting, motors (largest 60HP), and other misc. small loads. The AVR has not failed while in use under load but seems to fail either start up, shutdown, or when the generator disconnects from load (ATS transition). This problem started to happen a while (maybe 2 years ago) after the 400A output breaker melted due to a loose connection between generator and breaker which also melted a few low voltage wires (signal and battery charger from ATS) without damaging the AVR. The replacement AVR will work for a while and fail like the others. Anyone else have an issue with similar repeated AVR failures? What else can cause this issue?