Ipetu
Structural
- Jun 5, 2007
- 54
Existing 5.5"x5.5" x 15.5' long wood beam supported at the ends and an intermediate timber post at about 9' from one end. The intermediate post is to be removed. The existing beam has to stay in place and appropriate strengthening has to take place with steel sections (2 C channels) with depth less than or equal to 6" (152 mm). The beam supports two floors in a residential occupancy. Tributary width of the existing beam is 10' (3.0 m). The following loads were used 1.0 kPa for dead load and 1.9 kPa for live load. I assumed that the new channel sections will take all of the load. From a strength point standard channels will not work. I had to select a MC 150x22.5. However this resulted in deflections of L/170 for total load and L/259 for live load. Code limits for live load is L/360. So I chose a MC 150x26.8 (the largest 6" deep MC available). Now my deflections are L/203 for total load and L/308 for live load. Still not satisfying the L/360 code requirement.Questions:
1) Attributing some amount of load sharing to the timber beam will satisfy the L/360 code requirement. Is this correct?
2) During the actual construction I was planning on pushing the channels right up against the floor joists to ensure that the compression flange is laterally supported. However I read on a post sometime back the following "Make sure the beams are as high as they can go but do not try to
force the C Channel up to contact the floor joists becaue when you release the force the C channel will just pull the floor joists away. Just sung it up there as best as you can." What does the author mean exactly? Is there a real danger in pushing the channels to contact the joists?
3)The usual bolting for this type of work is to use 5/8" diameter threaded rod at 1' interval in a top and bottom staggered pattern. What is the science behind this? i.e. how is this determined?
4) Will the bolting mentioned in 3) above ensure that the compression flange is fully supported? If not how can support for the compression flange be achieved?
Thanks very much.
1) Attributing some amount of load sharing to the timber beam will satisfy the L/360 code requirement. Is this correct?
2) During the actual construction I was planning on pushing the channels right up against the floor joists to ensure that the compression flange is laterally supported. However I read on a post sometime back the following "Make sure the beams are as high as they can go but do not try to
force the C Channel up to contact the floor joists becaue when you release the force the C channel will just pull the floor joists away. Just sung it up there as best as you can." What does the author mean exactly? Is there a real danger in pushing the channels to contact the joists?
3)The usual bolting for this type of work is to use 5/8" diameter threaded rod at 1' interval in a top and bottom staggered pattern. What is the science behind this? i.e. how is this determined?
4) Will the bolting mentioned in 3) above ensure that the compression flange is fully supported? If not how can support for the compression flange be achieved?
Thanks very much.