We can’t answer that for you as we don’t know what the rest of your control circuit looks like and what you mean by “Remote”.
The Schneider ATS48 soft starter is not a VFD with flexible logic programming of inputs and outputs. For the most part, any control logic to select local or remote control is done in external wiring. The only possible exception is if you are using the comm port as a control source instead of wiring. If so, then you CAN reprogram Logic Input 1 to select for that possibility. Whether or not your starter has been programmed this way is something you will have to determine and to change it, read the manual.