Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

relief valves 1

Status
Not open for further replies.

roker

Chemical
Joined
Jun 23, 2004
Messages
198
Location
IL
how should be calculated the temperature at the outlet pipe from a relief valve for vapor/gas flow in case of fire or power failure?
is there a temperature gradient along the outlet pipe till the flare header?
 
roker,

I'm not sure of your application, but, normally, if there is a danger of heat and/or gas from a relief valve, the practice is to vent to the outside or to the stack (in the case of a furnace).
 
hello Josephn16,

what i ment is for example if a relief valve is set to 20 barg and 200 deg C what will be the temperature at the outlet of the relief valve when vapor or gas are discharged from the relief valve.

regards
 
Do an adiabatic expansion on the gas starting with the inlet conditions. You'll need a simulator or a Mollier diagram to estimate the outlet temperature on expansion.

A rule of thumb for cooling on expansion is about 7 deg F per 100 psi I believe (do a keyword search on the site, this has been discussed quite a few times).
 
Hi:

I thing that one way to estimate that temperature is getting entalphy from a Molliere Diagram as TD2K said, after that you can get the oulet temperature with 1 Bar (atmospheric pressure), starting with 20 barg and 200°C I got 160°C, assuming that the entalphy is constant.

Bye There
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top