Relief Valve Sizing for Vessels Containing Solids

Status
Not open for further replies.

apatjr

Electrical
Joined
Jul 16, 2001
Messages
25
Location
US
The thermal expansion calculations for pressure vessels are based on an empty vessel. If the empty vessel is in a fire and the gas stored starts to expand rapidly the relief valve will protect the vessel from damage.

However, what if the vessel is filled with a solid like desiccant in a heatless dryer. The desiccant pellets will occupy some of the internal space and reduce the volume of gas stored in the vessel.

Is there a correction factor that is applied to the relief valve orifice calculation to allow for the reduction in internal volume?

Thanks in advance for any thoughts.

 
Remember the ideal gas law?

Patricia Lougheed

Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.
 
For your first remark, it is very unlikely that a properly rated safety valve ( installed on fired and unfired pressure vessels) would protect a vessel from an external fire because they are not normally rated for a fire scenario.
For your second remark, a properly sized safety valve is rated based on its energy input (BTU/HR, LBM/hr) at a particular set pressure. It is independent of its volume but having said that it is possible that energy input may be proportional to size (volume) of vessel.
 