- Feb 2, 2003
- 11
Friends,
We have recd. a rental boiler for emergency heating steam requirements during the winter period. Boiler supplied is 300 psig rating and our existing system is 150 psig. Vender has offered to put a relief valve @150 psig on the steam outlet nozzle before the stop valve by providing a tee on the outlet nozzle. Is it acceptable from code point of view.
Boiler is designed to section I. As per ASME section I, PG-71.2 and PG-71.7 an independent connection is required for RVs. Can this be considered as an independent connection because as such there is no obstruction in the steam path to RV.
De-rating the boiler to 150 psi was the first option we thought of but since that requires re-registration we are trying to avoid that.
Two PSVs @300 will stay. Additional RV at 150 is to protect the existing system.
The boiler is oil fired (start up with propane).
My thoughts were that if we install the additional RV after the stop valve then we have to follow 31.1 which means 1 RV at 150 psi for the maximum flow is enough (Max capacity would be with the steaming capacity at 150 psi which will be more than the steamning capacity at 300 psi which can be calculated). BUT if the RV is before the stop valve probably we have to follow the rules of sec I which means 2 RVs (As per ASME section I, PG-67.1) and again if adding the RV on the outlet of main steam is acceptable.
This boiler is for Ontario, Canada.
Thanks a lot in advance for your advise.
Arvi
We have recd. a rental boiler for emergency heating steam requirements during the winter period. Boiler supplied is 300 psig rating and our existing system is 150 psig. Vender has offered to put a relief valve @150 psig on the steam outlet nozzle before the stop valve by providing a tee on the outlet nozzle. Is it acceptable from code point of view.
Boiler is designed to section I. As per ASME section I, PG-71.2 and PG-71.7 an independent connection is required for RVs. Can this be considered as an independent connection because as such there is no obstruction in the steam path to RV.
De-rating the boiler to 150 psi was the first option we thought of but since that requires re-registration we are trying to avoid that.
Two PSVs @300 will stay. Additional RV at 150 is to protect the existing system.
The boiler is oil fired (start up with propane).
My thoughts were that if we install the additional RV after the stop valve then we have to follow 31.1 which means 1 RV at 150 psi for the maximum flow is enough (Max capacity would be with the steaming capacity at 150 psi which will be more than the steamning capacity at 300 psi which can be calculated). BUT if the RV is before the stop valve probably we have to follow the rules of sec I which means 2 RVs (As per ASME section I, PG-67.1) and again if adding the RV on the outlet of main steam is acceptable.
This boiler is for Ontario, Canada.
Thanks a lot in advance for your advise.
Arvi