tickle, you are correct when saying that the PSV will provide certain level of protection if the PSV set pressure is close to the operating pressure (i.e. the relief temperature will be fairly close to the operating temperature and definitely well below the maximum wall temperature). However, it should be noted:
- Pressure-relief devices protect a vessel against overpressure only; they do not protect against structural failure when the vessel is exposed to extremely high temperatures such as during a fire. (API 520/I, Section 1)
- Temperature rise of the vessel metal cannot be assumed equal to the temperature rise of the fluid (gas) inside the vessel, due to very low heat transfer coefficients. Hence the calculated relief temperature of the gas inside the vessel will occur significantly after the vessel wall reaches the same (relieving) temperature. A characteristic of a vessel with an unwetted internal wall is that heat flow from the wall to the contained fluid is low as a result of the heat transfer resistance of the contained fluid or any internal insulating material. Heat input from a fire to the bare outside surface of an unwetted or internally insulated vessel can, in time, be sufficient to heat the vessel wall to a temperature high enough to rupture the vessel. (API 521, Section 4.4.13.2.3)
- An unwetted steel plate 25 mm (1 in.) thick takes about 12 min to reach 593 °C (1100 °F) and 17 min to reach 704 °C (1300 °F) when the plate is exposed to a typical open fire (Figure 1 and 2, API 521). This does not mean that the fluid inside the vessel will have the same temperature at the same time. As the fire continues, the vessel wall temperature and the contained-gas temperature and pressure increase with time. The PSV opens at the set pressure. With the loss of fluid on relief, the temperatures further increases at the relief pressure. If the fire is of sufficient duration, the temperature increases until vessel rupture occurs. (API 521, Section 4.4.13.2.4)
- Where a PSV alone is not adequate, additional protective measures should be considered, such as water sprays (see 4.4.13.2.6.2), depressuring (see 4.6 and Annex A), earth-covered storage (see 4.4.13.2.6.3), and diversion walls (see 4.4.13.2.6.4). Where there is insufficient time for operator reaction, then automated actuation of depressuring, water spray, or isolation should be considered. Obviously, where fire fighting facilities do not exist, depressuring is likely the only effective way to prevent from vessel rupture.
Installing fire case PSV on a vessel containing gas only or high boiling point liquid - while mandatory by the Codes - in most of the cases cannot protect the vessel from the rupture scenario. If we are interested in preventing from this actually happening, secondary measures must be provided.
Dejan IVANOVIC
Process Engineer, MSChE