The ASHRAE 15 addendums of 2000, numbers C & D , Appendix H shows the math that was endorsed for use for refrigerants and refrigeration type SRV's of the Pop Off- 25% +/- Blowdown, Direct Acting Types....The most common variety. Appendices tabulate this though a number of engineering firms have programmed the Network Math for multiple valves discharging at different set pressures to a common header.
There are other devices and alternative math...See the API 520 and articles in Semple, Anderson Greenwood and Crosby (manufacturers, Anderson Greenwood published in 1989, Chemical Engineering or proceedings of the AIChE though I don't have the specific source at this moment) and detailed what was the basis of concern for Petrochem and Air Cracking plants in tuilizing similar deep-blowdwon valves...
The authority on the evolution of the ASHRAE 15 to incorporate this approach was Mr. Wm V. Ricahrds of Illinois, consultant...
Follow up work by Mr. D. Kuespert of Snowy Owl LLC and others...Also consultant.