Suggestion: References:
1. ANSI/IEEE Std 242-1986, Section 11.4.5 Phase Balance Current Relay - Device 46.
2. ANSI C50.13-1977
Reference 1, industry standard, mentions Dev. 46 only. Unbalanced loads, unbalanced system faults, and open conductors, or other unsymmetrical operating conditions result in an unbalance of generator phase voltages. The resulting unbalanced (negative sequence) currents induce double system frequency currents in the rotor that quickly cause the rotor overheating. Serious damage to the generator will occur if the unbalanced condition is lasting. The ability of the generator to withstand these negative sequence currents is defined by Reference 2 as I2**2 x t =K. Generators under 100MVA are generally able to carry negative sequence currents up to 8-10% of full load current continuously within tolerable overheating.
Usually, a negative sequence relay, which consists of time overcurrent unit with extremely inverse characteristics matching the generator I2**2 x t curves, is recommended. Static types of the relay are more sensitive capable of detecting negative sequence currents down to the continuous capability of the generator.