wcaseyharman said:
Do you mean that I don't need to change the setting pickup value?
Here's what I calculate and my assumption (please CMIIW)
Currently, the setting pickup value (I_Pickup_Percentage Differential) is 0.1 Ie (Ie = 5 A)
The ratio turns of CT are 300:1 (HV side) and 3000:1 (LV side)
The primary side of MTR (150kV) CT2:
I_1 primary CT = 206.7 A
I_1 secondary CT = 0.6546 A
The secondary side of MTR (11kV) CT6:
I_2 primary CT = 2818.52 A
I_2 secondary CT = 0.8925 A
The slope setting is 10% and 65%
SST (on secondary side of CT):
I_3 primary CT = 26.24 A
I_3 secondary CT = 0.00875 A
Since the I_3 secondary CT is lower than 0.5 (0.1 Ie which is the setting pickup value), my conclusion is: It is safe to install the 87T between CT2 and CT6 when generator stand-still
Please tell me what's wrong with my calculation and obviously my conclusion.
Thanks.
(Here's the simulation that I tried)