Two very different questions have been asked.
The reinforcement requirements for a concrete foundation depends upon the degree of foundation 'stiffness required and characteristics of concrete (shrinkage). A minimum amount of reinforcing is always required but, the amount of foundation 'stiffness' will usually control the final amount. Of course, we are not trying to overcome bad subgrade problems by adding more reinforcing steel but, working on improving the subgrade soils with the structural fill.
The amount of settlement the foundation will undergo is a function of the applied building and live loads and the characteristics of the supporting soil.
You say the site has structural fill. The structural fill has been compacted and is 'certified as capable of supporting 150 Kpa'. How much settlemnt was considered acceptable at this load? You must remember that soil is a compressible, variable material.
What are the inplace conditions of the underlying soil? The whole fill matte may undergo settlement due to compressible or worse subgrade soils. Is this possible subgrade settlement figured into the fill 'capacity?
The amount of reinforcing steel in the foundation can only affect differential foundation settlement, depending on how 'stiff' the foundation is designed.
The Structurals on this site can provide some reinforcing information but, You will need to provide some more information regarding the structure, single story?, 2 or 3 story? Construction type?