nagatalluri
Geotechnical
- Jul 19, 2010
- 83
Guys
I am checking the design for substation foundation. The designer came up with minimum reinforcement as 1.56 in2 (top/bottom). He is using # 8 bar top and bottom. f we sum the areas then it meets the requirement, if not it is half of the required. (#8 bar area 0.79in2 where as required is 1.56in2).
Is it it ok to sum the bar areas from top and bottom or the requirement have to be met individually.
Please let me know
Thanks
NT
I am checking the design for substation foundation. The designer came up with minimum reinforcement as 1.56 in2 (top/bottom). He is using # 8 bar top and bottom. f we sum the areas then it meets the requirement, if not it is half of the required. (#8 bar area 0.79in2 where as required is 1.56in2).
Is it it ok to sum the bar areas from top and bottom or the requirement have to be met individually.
Please let me know
Thanks
NT