Three primary considerations for the slab are:<br>--Strength of the subgrade/subbase<br>--Strength of the concrete<br>--Magnitude and type of loading<br><br>Since your loading is uniform and the slab is ground supported, there isn't much need for reinforcement other than to control shrinkage cracks. Assuming your liquid level doesn't exceed about 20 feet, you will have a uniform load of about 1250 psf (assuming Sp. Gr. = 1.0 (water))At or below this value, it isn't necessary to consider slab bending assuming your modulus of subgrade reaction, K, is greater than about 150 pci. <br><br>I would suggest a minimum concrete strength of 4000 psi, using as large an aggregate as practicable. Reinforcement would likely consist of at least one mat of 6x6-W4.0 x W4.0, placed at the center of the slab. The slab thickness would likely be in the 6-inch range, but you can check that analytically through any of the pavement slab design procedures (contact pressure = 1250 psf or whatever it happens to be). A good reference for this is "Slab Thickness Design for Industrial Concrete Floors" by Robert G. Packard, Portland Cement Association, Skokie, Il.<br><br>This is a variation on a pavement thickness design problem.