Not really enough information provided to tell one way or the other. Have no clue if you're using 6" block, 8" block, 12" block. Don't know boundary conditions. Don't know what, if any, axial loads there are to contend with. May very well be fine, that's a lot of reinforcing and a relatively small 15' span.
Not sure I understand your loading criteria though. Are you saying a constant 3 psi for 40 ms and then drops to zero? I'm not familiar with any standard blast loadings that take this form, should be a peak pressure that dies out quickly and then goes into a negative rebound phase. If that 3 psi is your peak pressure and then dies off over 40 ms then what you have would very likely be overkill. 3 psi is pretty small peak pressure as far as blast is concerned.