I need the collective wisdom of those who frequent this site regarding the connection between a reinforced CMU shear wall and a cast-in-place reinforced concrete (RC) foundation wall.
With a reinforced CMU shear wall, ACI 530-02 limits the steel stress (grade 60) to 24 ksi.
In trying to determine the proper embedment length for the chord dowels in the RC foundation wall, as well as the design tensile force in those dowels (for a post-installed situation), would it be acceptable to apply the 1.6 load factor to the ASD stress to evaluate the dowels under 318-02?
Given #7 bars (As = 0.60), ASD tension force would be 0.60 * 24 ksi = 14.4 kips. Force applied to the dowels under ACI 318-02 would be 14.4 kips * 1.6 = 23 kips.
I am most concerned about the post-installed dowels as it is not possible to fully develop the #7 using an adhesive anchor such as Hilti's HIT-HY 200.
Your thoughts?