Feb 19, 2015 #1 siwan Electrical Joined Nov 18, 2011 Messages 2 Location IN I am facing problem of regular failure of LVDT transducer in hydro project .The aux supply voltage is 24 volt DC .We have connected -ve of the 24 volt Dc to the ground . The grid resistance of earth mat is 2 ohm . Pl. suggest some solution
I am facing problem of regular failure of LVDT transducer in hydro project .The aux supply voltage is 24 volt DC .We have connected -ve of the 24 volt Dc to the ground . The grid resistance of earth mat is 2 ohm . Pl. suggest some solution
Feb 19, 2015 #2 Skogsgurra Electrical Joined Mar 31, 2003 Messages 11,815 Location SE Are you suggesting that there is a potential difference that kills the LVDT? That should be very easy to verify with an ordinary volt-meter. I really hope that you are nut running the LVDT on DC. That will kill it. They are usually supplied with a few volts at 1 - 10 kHz. Gunnar Englund http://www.gke.org-------------------------------------- Half full - Half empty? I don't mind. It's what in it that counts. Upvote 0 Downvote
Are you suggesting that there is a potential difference that kills the LVDT? That should be very easy to verify with an ordinary volt-meter. I really hope that you are nut running the LVDT on DC. That will kill it. They are usually supplied with a few volts at 1 - 10 kHz. Gunnar Englund http://www.gke.org-------------------------------------- Half full - Half empty? I don't mind. It's what in it that counts.