Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Reference for wet bulb calculation

Status
Not open for further replies.

jnh11564

Electrical
Aug 6, 2010
1
I'm wondering if someone can provide a reference for the wetbulb calculation provided by M777182 in thread 724-129442. The calculation is as follows:

m777182 (Chemical) 20 Jul 05 6:35
On a range Tdry bulb=15..40[deg C] and rh=10...90[%]you can calculate the Twet bulb[degC] at P=1006[mbar](=755 Torr)with max relative error~6% with an approximative polynomial model that you can put in a cells. For lower Tdry and rh the relative error will be higher.

Twet bulb= A*Tdry + B*rh + C*Tdry^2 + D*rh^2+ E*Tdry*rh + F whereA=5,391260E-01B=1,047837E-01C=-7,493556E-04D=-1,077432E-03E=6,414631E-03F=-5,151526E+00

Thanks!
 