ruggedscot
Electrical
- Feb 17, 2003
- 416
Recently discovered an error that has been present for over 5 or 6 years now with a set up. We have identified that we have multiple neutral earth points inadvertently installed on a power distribution system. My question on this involves the CT set up - if we have been running with the neutral earth both before and after the CT set up then will this have had an effect on the relay protection ? I would tend to look towards having the CT and REF systems all checked and injection tested after removing the erroneous N-E link before swinging into service again. Has anyone come across this sort of error before and what was their experiences of this in the long run.
N-E link at the transformer and N-E linked again in the switchboard. Section of busbar linking the transformer with the panelboard.
N-E link at the transformer and N-E linked again in the switchboard. Section of busbar linking the transformer with the panelboard.