I just had a similar discussion with a client the other day andhe statement can be somewhat ambiguous and needs to be confirmed with the client. Their reasoning was:
- 100% redundancy means if anything fails 100% capacity is available, ie two units at 100% capacity, 3 units at 50% capacity, 4 units at 33% capacity etc
- 50% redundancy means if anything fails min 50% capacity is available, ie two units at 50% capacity are required (or 3 at 33% etc)
For this particular project the requirement was 75% redundancy so four units at 25% full load are being installed, if any one fail 75% capacity is available which is still sufficient for most of the time.