I was wondering, if during a ground fault on the primary of a 44 kV transformer in a substation, if the system feeding the fault is a 3 Ph 4 wire system and the fourth wire could be either Neutral or ground and this wire is connected to the grounding grid being designed.
Major part of the ground fault current will flow back through this fourth wire. I was just wondering, when I have to consider fault current for GPR calculation, Will IEEE, inspection authoritry or common sense allow the design of grid based on the current flowing through the ground grid(earth) rather designing based on total ground fault.
Will it matter if the forth wire from the utility is a Neutral or ground.
I was wondering, if during a ground fault on the primary of a 44 kV transformer in a substation, if the system feeding the fault is a 3 Ph 4 wire system and the fourth wire could be either Neutral or ground and this wire is connected to the grounding grid being designed.
Major part of the ground fault current will flow back through this fourth wire. I was just wondering, when I have to consider fault current for GPR calculation, Will IEEE, inspection authoritry or common sense allow the design of grid based on the current flowing through the ground grid(earth) rather designing based on total ground fault.