Evgueni
Electrical
- May 30, 2006
- 7
Hello Gentlemen
It is my first time here.
There is short history about my problem. This project has radial distribution power system with the following voltage levels 115 kV , 13.8 kV , 4.16 kV , 0.48 kV.
After S.C. calculation I got S.C. as 30.7 kV r.m.s. on the bus 0.48 kV hich is connected with transformer 13.8/0.48 kV , 1600 kVA , Z%=6 , X/R=7.1 . Some loads connected with this transformer has very small value ,
as 1.5 kW. For this load the cable sizes 12 AWG or 10 AWG are reasonable .
To calculate cable current- thermal capability to withstand impact of the S.C. I used Std. 242-1986 p.328 formula (ICEA P-32-382-1969 [5] : Is.c.=CM/SQRT(Tf*Fac/(0.0297*LOG10((250+234)/(90+234))))/1000 ,
· For fault duration Tf I used 0.026 sec or 1.56 cycle
· Skin effect Fas was assumed as 1
· CM- was taken as 6529 Circular mils for 12 AWG
After calculation I got value as 2913 A or 3 kA for cable 12 AWG , so for
this particular case I have to reduce S.C. value from 30.7 kA to 3 kA (see
att.A)
1 question : Is it possible to reduce S.C. from 30.7 kA r.m.s. to 3 kA r.m.s. ?
2 question : If yes , could I make it by LV breakers with incorporated S.C. limiters or similar devises ?
3 question : If no , which alternative solution could I us ?