Eccentric reducers (when required) should be and will be installed with the flat side up no matter where the suction comes from.
Where a static suction head will exist the pump suction piping should slope continuously downward to the pump... If the source of supply is above the pump, the straight side of the reducer should be at the bottom (Fig. 9). Installing eccentric reducers with a change in diameter greater than 4 in (10 cm) could disturb the suction flow. If such a change is necessary, it is advisable to use properly vented concentric reducers.