I'm analyzing a maintenance catwalk (designed and fabricated by never installed) for use as a small pedestrian bridge. Span will be about 30' to cross a drainage ditch between the parking lot and industrial facility. I've run the analysis and it doesn't quite work considering the 90psf load from the AASHTO pedestrian bridge specs. This thing is only 3 feet wide - no passing. It's also not in an area that would be subject to crowd loading. 90psf seems excessive to me in this instance. If you assume 250# workers walking in a single file line on the bridge with 3ft per person, you have 250#/9ft2 = 27.778psf. I wouldn't drop it this low, but given the relative predictability of the usage here what are the general thoughts about reducing to 40psf?
Vibrations is another issue. In this case, I'm inclined to give a warning that it is likely to vibrate - either spend the money to fabricate a new structure or put up with vibrations. The girders are W12x14's. They are thoroughly braced and strength is no issue, but it's flexible. A quick rundown of the DG11 checks for approximate natural frequency and acceleration puts my minimum Ix at about 1110in4 to be within the suggested limits for an outdoor pedestrian bridge.