I'm afraid you can not use such a curve. Each secondary of a three winding rectfier transformer is just rated for half of the total power.
Using such transformers I have usually applied the following kind of protection:
- current transformers on each secondary, connected to the rectifier control unit which was able to trip the primary circuit breaker via a undervoltage release coil in case of a failure
- additionaly the primary ciruit breaker was set up to trip on very large fault currents