Dear Mr. edison123
Mr. scottf suggests
Q1. "...Why not just buy 11kV/15kV class window-type CTS, or block type CTs ..."
A1. Agreed in full, as there seems to have room for it. The only consideration is the "cost" which may be 1000% times. It is NOT "costly" consider that the present setup is a big time-bomb!.
A2. An alternative is to remove all the LV CTs from the fiber board, sleeve them over the b]insulated[/b] cables, [observing the creepage and clearance distances].
Caution: See following learned advice:
a) Mr. ppedUK " ..On anything above 1kV system voltage, you would only ever use a ring CT such as that over an insulated bushing, and then, more often than not, also with an earthed metallic (non-ferrous) sleeve between the bushing and the CT, such that there is almost no chance of a flash-over to the CT...."
b) LionelHutz " ...UL 347 5.14.201 has clearances. It's for switchgear but a connection box is a similar type of gear. 4" clearance and 7" creepage except to enclosure walls which is 6" clearance and 8" creepage..."
Che Kuan Yau (Singapore)