Most of our distribution is multi-grounded, but in some areas, that is not very good, you know sand, or rock. But we have had problems balancing distribution circuits, so we do use a ground setting higher than 2/3. Actually we have seen large load changes from season to season, and around holidays. As a dual peaking utility, it is hard to predict between compressor AC and electric heat, and holiday lights to the max.
We also have a few old delta circuits, where the ground fault currents calculate to about 5 amps, which is hard to detect and it has started fires.
My old company had tried covered conductors years before I worked there. They looked bad as the insulation was pealing off, or hanging off the wire. That's my thoughts on it.
But now the company I work for only has 30 foot right-of-ways, so they can not trim outside of that, and we still get trees bending so much in the wind to come into contact. The customers want us to underground the old lines, but don't want us to dig up the tree roots, and don't like the green boxes.
Though we have more problems with animal contacts, where people feed the things. Tree wire does not fix this, and animal guards only work so-so.
A comment on negative sequence, most three phase solar inverters do not create negative sequence into a fault, so you can't depend on them for that, or those for directional support.