Situation:
Cylinders for columns failed to achieve strength at 28 days. Contractor wants to run rebound tests to ascertain strength of the columns.
I have made some calculations for Schmidt hammer test. As per ASTM C805 and ACI 228.1, correlation curves have to be established for each type of mix design for which the tests are intended. I followed the below procedure;
1. Took 3 cylinders at 7 days for the same class of concrete poured in the structure (60 Mpa flowable); Marked 15 points on each cylinder 50mm and 120 degrees apart. Ensured 15% of load is applied on the cylinder in the compression machine. Then 15 rebound readings were taken. Average was calculated. Similar procedure was followed for 3 cylinders @ 28 days.
2. Later the cylinders were tested in compression and recorded the strength.
3. Plotted Rebound Numbers Vs Compressive Strength for each cylinder.
4. A correlation curve was established.
5. Site readings were taken on the structure to compare with the correlation curve to establish the strength of the concrete in the structure.
Kindly let me know the correctness of the above procedure. Some people say that the correlation curve is on the Schmidt hammer and the strength shall be calculated from the curve, but I believe that curve is not applicable for every concrete grade and may not represent the actual strength.
Cylinders for columns failed to achieve strength at 28 days. Contractor wants to run rebound tests to ascertain strength of the columns.
I have made some calculations for Schmidt hammer test. As per ASTM C805 and ACI 228.1, correlation curves have to be established for each type of mix design for which the tests are intended. I followed the below procedure;
1. Took 3 cylinders at 7 days for the same class of concrete poured in the structure (60 Mpa flowable); Marked 15 points on each cylinder 50mm and 120 degrees apart. Ensured 15% of load is applied on the cylinder in the compression machine. Then 15 rebound readings were taken. Average was calculated. Similar procedure was followed for 3 cylinders @ 28 days.
2. Later the cylinders were tested in compression and recorded the strength.
3. Plotted Rebound Numbers Vs Compressive Strength for each cylinder.
4. A correlation curve was established.
5. Site readings were taken on the structure to compare with the correlation curve to establish the strength of the concrete in the structure.
Kindly let me know the correctness of the above procedure. Some people say that the correlation curve is on the Schmidt hammer and the strength shall be calculated from the curve, but I believe that curve is not applicable for every concrete grade and may not represent the actual strength.