Penpendrum
Civil/Environmental
- Sep 30, 2012
- 48
The ACI code gave a provision on structural integrity to perimeter beams is to splice continuous top bars at mid span and splice continuous bottom bars at or near supports. Under gravity loads or in most cases the top bars at mid span and the bottom bars near the supports (in a doubly reinforced beams ) receives compressive stresses. My question is : if I have 3 top bars and the two top bars ( at the sides ) are made continuous , do we need to stagger the splices? if so, what provision in the ACI code allows this? and do we really need to splice (class B tension lap splice) =it exactly at mid-span?
And also at the bottom bars .
If I made 2 bottom bars continuous and I had to splice near the column,do I need to stagger the lap splicing? I have seen a link that it is allowed not to stagger it. but I do not know in what section of the code allows it. here is the link . I wonder what section of the aci code allows this?
the ACI code clearly states that at non-perimeter at least two bars or at least 1/4 of Area of rebars must be continuous or splice(class B tension lap splice) over the support. Do we really need to interpret this Literally?I mean do we really need to splice it exactly over the support when needed? technically this produces a lot of waste if we should strictly follow this.
Please!! I need clarifications if this statements of the ACI code must be interpreted literally. Please guide me with this provisions.
And also at the bottom bars .
If I made 2 bottom bars continuous and I had to splice near the column,do I need to stagger the lap splicing? I have seen a link that it is allowed not to stagger it. but I do not know in what section of the code allows it. here is the link . I wonder what section of the aci code allows this?
the ACI code clearly states that at non-perimeter at least two bars or at least 1/4 of Area of rebars must be continuous or splice(class B tension lap splice) over the support. Do we really need to interpret this Literally?I mean do we really need to splice it exactly over the support when needed? technically this produces a lot of waste if we should strictly follow this.
Please!! I need clarifications if this statements of the ACI code must be interpreted literally. Please guide me with this provisions.