I have a 5' high, 8" thick, cast-in-place cantilever retaining wall. The contractor installed the footing dowels with the vertical leg of the bar 3" too short to have a proper "Class B" tension lap with the vertical bars of the wall.

Is there a procedure to calculate a reduced capacity of the wall based on this improper lap length?
 
I'd reduce your available steel tension capacity by the same percentage that the lap length has been reduced. Here, that will result in a reduction of moment capacity by the same percentage +/-.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
I generally echo KootK's approach. For me though, if the actual bars were #6 (.44 in^2) and As,pro/As,req landed me at .38 in^2, I would round down to .31 in^2 (#5).