Section 517.30(C)(1) requires separation of the emergency circuit wiring from the normal circuits. This is to reduce possibilities of a failure in a normal circuit causing the failure of an emergency circuit.
waross said:I have more than once seen situations where an overloaded generator caused the destruction of an ATS in minutes.
You don't want a fault on the normal system to take out a life safety ATS.
A fire may compromise a normal duty feeder and damage the ATS. You want the life safety ATS to be independent.
Yes. The transfer switch is part of the separated system.Mbrooke said:Sure- and I would think same protection is afforded by having two systems separated from one another.
The overload slowed the generator down.
The transfer switch dropped out, drawing heavy current across the contacts.
The generator recovered.
The transfer switch dropped out, drawing heavy current across the contacts.
The generator recovered.
Repeat.
While the current was well within the breaking capacity of the ATS and below the capacity of the generator breaker, the repeated breaking without an adequate cool down time melted the contacts.
The cycle eventually stopped when there was no longer enough of the contacts left to make contact.
I have installed a lot of transfer switches and have never seen one with self protection.
The transfer switch should be sized to be adequately protected by the mains protection or by the generator protection already in place.
the life safety branch .... these loads would include a very small percentage of a hospital’s total electrical system, typically 5% to 10% at most
Where life safety power would only be 5% of the building’s power requirement, the critical power system of a hospital could easily account for 25% or more of a hospital’s total power requirement.
The equipment system can easily account for 30% or more of the overall hospital electrical system.
In summary, the total amount of emergency power for most buildings (and therefore the amount of emergency distribution equipment needed) is typically 10% or less and consists of only that minimal amount of power needed to help people safely exit a building within the first few minutes of normal power interruption. For hospitals, emergency power becomes the life blood of a building without utility power and must be maintained throughout a power outage, which could last for days after a storm or other catastrophic event. As a result, it’s not unusual to see the emergency power of a hospital exceed 50% or 60% of the building’s total power needs. Also, as separate transfer switches are need for each type of load (life safety, critical, nondelayed automatic equipment, delayed automatic equipment, and delayed automatic or manual connection equipment loads), multiple ATSs are always needed for hospitals. For a 200,000-sq-ft hospital, eight or more transfer switches could be used. A similarly sized office building would typically have only two ATSs.
CEC 2015 said:Vital branch — the portion of an essential electrical system in which the circuits require power restoration
within 10 s.
I don't see anything in the Canadian code to prevent one generator and one transfer switch for a small hospital.CEC 2015 said:24-304 Transfer switches (see Appendix B)
(1) All transfer switches shall comply with the requirements of the supply authority.
(2) Automatic transfer switches used in essential electrical systems shall conform to the requirements of
CSA C22.2 No. 178.1 and, in addition, shall
(a) be electrically operated and mechanically held; and
(b) include means for safe manual operation.
(3) Manual transfer switches shall conform to the following:
(a) the switching means shall be mechanically held and the operation shall be by direct manual control
or by electrical remote manual control utilizing control power from the supply to which the load is
being transferred;
(b) a manual transfer switch that is operated by electrical remote manual control shall include a means
for safe manual mechanical operation;
(c) reliable mechanical interlocking (and, in the case of a switch operated by electrical remote manual
control, electrical interlocking) to prevent interconnection of the normal and the emergency supplies
of power shall be inherent in the design of a manual transfer switch; and
(d) a manual transfer switch shall include a readily visible mechanical indicator showing the switch
position.
(4) The vital and delayed vital branches shall be connected to the emergency power supply by means of one
or more automatic transfer switches.
(5) The conditional branch shall be connected to the emergency power supply by either a manual or an
automatic transfer switch.
I've seen some interesting interpretations of NEC requirements for hospitals by local AHJ. Some real head-scratchers.