Hi Electrical people! I was hoping someone could explain how to calculate the power usage of (in this case) a large air-compressor.
I've been told the voltage across the unit is 453V and the current draw is 596A . Now I am assuming this is a 3 phase unit, and the current stated is per phase- but I honestly do not know.
The power factor I've been given is 0.91, but no matter how I try to calculate the power (whether it be using RMS voltage and RMS current ....) I cannot come up with the answers they get which are (and there are two different ones) 407.4 kW and 409.4kW
The way I calculated it was...
P=Pf * (V*I*3)/2 =368.5kW (where the 3 comes from 3 phase power, the two is from RMS voltage and Current (root 2 squared), and Pf is the power factor. Perhaps I'm leaving something out?
Any insight would be appriciated!
Cheers
James