Hello,
I am trying to decipher an Eaton/Cutler-Hammer TCC. The drawing number is 70C1034 and it is for a Digitrip 1150 trip unit.
The problem I have is a heater shorted out and instead of tripping the 30A MCCB in the unit or the 50A panel MCCB, it tripped the 800A distribution LVPCB. It tripped at 1707A on an inst trip. I have plotted the TCC s but do not understand the inst portion of the curve.
I was told that the Inst. region actually goes all the way down to the current axis with the understanding that there is a “minimum time” that it will take for the breaker to trip. That being said, what is the purpose of what appears to be the adjustable Minimum Clearing Time on the lower side of the inst. region? Am I better off adjusting the short pick-up or the short time? I guess I always thought you could adjust the short time up and raise the inst portion up so the inst portions of the downstream breakers don’t overlap.
Just for clarification the short slope is flat.
I am trying to decipher an Eaton/Cutler-Hammer TCC. The drawing number is 70C1034 and it is for a Digitrip 1150 trip unit.
The problem I have is a heater shorted out and instead of tripping the 30A MCCB in the unit or the 50A panel MCCB, it tripped the 800A distribution LVPCB. It tripped at 1707A on an inst trip. I have plotted the TCC s but do not understand the inst portion of the curve.
I was told that the Inst. region actually goes all the way down to the current axis with the understanding that there is a “minimum time” that it will take for the breaker to trip. That being said, what is the purpose of what appears to be the adjustable Minimum Clearing Time on the lower side of the inst. region? Am I better off adjusting the short pick-up or the short time? I guess I always thought you could adjust the short time up and raise the inst portion up so the inst portions of the downstream breakers don’t overlap.
Just for clarification the short slope is flat.