Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Read-Only RSLgix 5

Status
Not open for further replies.

modhauler

Electrical
Joined
Jun 19, 2003
Messages
4
Location
US
I am trying to set-up a read-only version of Rockwell RSLogix-5 software for my technicians to use to troubleshoot our processes without having the ability to do anything other than read logic and data table values: no changes allowed. I've tried the RSLogix program/file passwords, but when I go online, it defaults to class 1 with all the priveledges. Lower class defaulting only seems to work in offline mode. Is there a way (start-up switches, other vendor products) that will provide me with a solution? We are also looking for this for RSLogix 500 as well.
Thank You in advance for your help..
John Hellmers
 
In RSLinx if you right mouse click on the processor and "View Ladder Code" allows for view only. I am using 2.53 rslinx and I know that it worked in most previous versions but was broken in a few in between. This should be enough for them and logix 500 I think does not even need to be loaded.
 
Try taking a look at RS Ladder, let someone look at the PLC logic.

Rockwell used to bundle it with some other products, check with your AB rep for a demo if one exists.

Hope that helps.
 