RCD and 0.75kw motor?
dave11282
GB
Hi all
I am using a single phase TEC 0.75kw motor on 240v 50Hz UK supply.
every time we drop the supply to the motor the 30mA RCD trips?
I know motors can be electrically noisey, but is there a simpler way around this apart from upping the RCD to say 100mA??
Does anyone know where TEC motor are made? URL?
thanks
Dave
Hi Dave
We supply TEC motors...mainly the three phase though, because they are a CHINESE made motor, and we find that the chinese have not yet perfected the manufacture of capacitors, and have a rather heavy failure rate!
As for the RCD tripping.....have you carried out an earth test on the motor, and if so, what readings are you getting?
regards
Jeff
Dave; It is not noise, it is "leakage" that is tripping your RCD (if RCD means ground fault protection). Your motor's insulation may be failing.
Keith Cress
Flamin Systems, Inc.-
many thanks guys,
Jeff,
I did carry out IR test, 800 meg ohm.
Do you have URL for TEC?
thanks
Dave
we also noticed that the new TEC we had in was now wound differently to the one we evaluated.
Which surprised us! The connections are different in the motor terminals.
Same 0.75kw spec / chassis
Dave