I have a client who would like me to design some attachments of their rain screen product to a precast concrete panel system (basically fancy siding). I am trying to figure out what wind loads I would apply to the the rain screen panel. I am currently using ASCE7-05 C&C loading on a 74' tall structure with a wind speed of 100mph which results in a pressure of 35.8 psf when I use GCpi=0 (I think the system is pretty porous).
I know this is the load that the precast panel must be designed for (not my concern) but I am not sure if the "Skin" of this panel must be designed for the same loading criteria? How would others interpret this condition?
FYI, this load is killing the design of the clips that the panels uses to attach to the precast panel (stress is 183 ksi in the clips with this loading).
I know this is the load that the precast panel must be designed for (not my concern) but I am not sure if the "Skin" of this panel must be designed for the same loading criteria? How would others interpret this condition?
FYI, this load is killing the design of the clips that the panels uses to attach to the precast panel (stress is 183 ksi in the clips with this loading).