Feb 3, 2022 #1 MaxMedic Civil/Environmental Joined Feb 3, 2022 Messages 17 Location US I cannot find resources for railing post embedment in concrete and railing strength. There is a 1.5" DIA. railing pipe post embedding into a ramp.
I cannot find resources for railing post embedment in concrete and railing strength. There is a 1.5" DIA. railing pipe post embedding into a ramp.
Feb 3, 2022 2 #2 SJBombero Structural Joined Dec 1, 2014 Messages 174 Location US Here is a calc sheet I made. It has references from various resources. https://files.engineering.com/getfi...7e0&file=Handrail_POST_EMBED_IN_CONC_PVC.xlsx Upvote 0 Downvote
Here is a calc sheet I made. It has references from various resources. https://files.engineering.com/getfi...7e0&file=Handrail_POST_EMBED_IN_CONC_PVC.xlsx
Feb 3, 2022 #3 dik Structural Joined Apr 13, 2001 Messages 26,109 Location CA Thanks... I'll take a look at the sheet. Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better? -Dik Upvote 0 Downvote
Thanks... I'll take a look at the sheet. Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better? -Dik
Feb 7, 2022 Thread starter #4 MaxMedic Civil/Environmental Joined Feb 3, 2022 Messages 17 Location US Thank you very much, I will look further into this. Upvote 0 Downvote
Feb 7, 2022 #5 dik Structural Joined Apr 13, 2001 Messages 26,109 Location CA I took a look at the sheet, and it's nicely done. Thanks for posting. Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better? -Dik Upvote 0 Downvote
I took a look at the sheet, and it's nicely done. Thanks for posting. Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better? -Dik
May 12, 2022 #6 KaBone Civil/Environmental Joined Feb 16, 2009 Messages 64 Location US Is there a factor of safety on the spreadsheet? Upvote 0 Downvote
May 13, 2022 #7 SJBombero Structural Joined Dec 1, 2014 Messages 174 Location US The calculations are done using LRFD principles and strength formulas found in ACI 318. They are not called safety factors any more but they function similarly. Upvote 0 Downvote
The calculations are done using LRFD principles and strength formulas found in ACI 318. They are not called safety factors any more but they function similarly.