Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Radial influence from drilled pier (caisson) 1

Status
Not open for further replies.

hopetolearn

Geotechnical
Nov 2, 2007
2
I have a project where there are existing utility vaults and basements within a distance 1 to 2 times the diameter of proposed caissons. How do I calculate the surcharge on the existing features from the proposed caissons? Any help would be highly appreciated.
 
Replies continue below

Recommended for you

I should add that the caissons are laterally loaded. Thanks
 
Here's one approach. Analyze the drilled shaft with a program that gives soil reactions, such as LPILE or COM624, as though the vaults didn't exist. Then re-analyze, cranking up the stiffness of the soil in the vicinity of the vault. Take your worst case soil reactions and apply them as a vertical line load to the side of your vault. You'll need to judge the width of wall that contributes in resisting the additional line load.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor