Correct Travis I don't have multiple supplies only the pump and city water. Ok so I have calced each system separately that is done, so I will just save as and create another file and then copy and paste my rack calc into my main overhead calc.
I assume I only copy the rack sprinkler nodes and piping nodes that I am calculating up to the connection point of my overhead system?
So once I achieve that I guess my goal is to manually balance the calc so the safety margins are within .05psi of both calcs?
I've got the logistics, mostly it's just the process.
Thanks VERY much for the help!