Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

R22 compressor used with R12

Status
Not open for further replies.

pardal

Automotive
Joined
Oct 17, 2001
Messages
444
Location
AR
Due not known razon it is a water chiller with out its compressor.

The facts are as follow :
Home made or a little shop done.
All presostats are setup for R12 pressures.
High press set point 225 # (pd/sq inch)
Low press set point to control the system 32 #
Low press set point to avoid runing without gas 6#
The suction and discharge pipes have ROTALOC as the ones pertaining to COPELAMETIC.
Air condensed.
Termic relay rated at 5,5 AMP
Voltage 3 x 380V 50 Hz
I have no idea about waterflow .
Output chilled water temp: 4 °C

All seem to be that a 500 series COPELAMETIC or 5Hp.
It was a way of work here to use a R22 compressor but runing it on R12 because to this HP rate a 5HP R22 comp is cheaper than a 4 HP R12 compresor , and in our country there where not any COPELAMETIC Compressor for R12.


My corncern is , what is the rated capacity when any given R22 compressor is run with R12?? .

Thank in advance.










Pardal
 
I DID A MISTAKE .


It should be a COPELAWELD no a COPELAMETIC.

Pardal
 
I did a quick calculation considering 00C evaporating temperature and 30 0C condensing temperature, neglecting subcooling and superheating at condenser and evaporator respectively. The power consumption drops by 4% when used with R12. Compression ratio is almost same for both R12 and R22. But you should change the expansion device.Discharge pressure of 225PSI seems to be quite high.

Regards,


 