"Modificatopn" of Hazardous Zones

Status
Not open for further replies.

pristava

Industrial
Joined
Jan 8, 2004
Messages
53
Location
US
European Standards provide "Concept of Walls" to modify Hazardous Areas. For the light gases, a wall located close to the potential gas leak makes hazardous area on the top of the wall,plus little beyond but generally another side of the wall is unclassified area.
/Book - A.Mc.Millan "Electrical Installations in Hazardous Areas"/
I am checking American Standards - API, NPFA but I didn't find this concept here.
Is this "Concept of Walls" is covered by International ISO Standards.
Our problem - Hazardous Area Zone2 (light gas leak) goes 3-4 ft beyond a fence where is private property.
 
I would suggest that you check the standard used to specify the hazardous area as many have recently been revised (e.g. IP-15 in 2002). A review based on the latest standard and accurately locating the specific release source may relocate the hazardous area boundary within your fence.

For example, a natural gas leak from a piping flange etc. would typically be only 1.5m radius under IP-15(2002).

See if some remedial work is possible to reduce the size and location of the hazardous area, e.g. restricting the size of the release or relocating the release point.



 