Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

"L class" vs "C class" for CT

Status
Not open for further replies.

tem1234

Electrical
Jun 13, 2007
192
Hi,

I try to understand what's the difference between a C800 and a 10L800 CT.

From what i understand, it's pretty much the same thing, considering 10% error on the C class.

I think the L class is from an old standard, ASA (american standard association), and the C class from a new standard IEEE.

So, is it normal to buy a new breaker in 2013 and to have L class CT in the bushing?

Thanks

 
Replies continue below

Recommended for you

The "L" class is used by CSA today. C800 and 10L800 are essentially the same thing.

For the "L" class in CSA, there also exists a 2.5L, which works the same way, just with an accuracy limit of 2.5% at 20 times Inom @ rated burden.

 
Thanks scottf

I found the CSA standard that talk about that.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor