In SW Florida the "first flush" is calculated thus -
Either the first 1/2" of runoff from the whole contributing area or the runoff from the first 1" of rainfall, with DCIA being considered separately, for percolation systems, which percolate within 72 hours with 100% Safety Factor.
For wet detention treatment, the treatment volume is doubled and 1/2 the volume must be released within 60-72 hours. 30% littoral shelf required. anti clogging device on drawddown orifice required.
(For systems that discharge to Outstanding Florida Waters, increase the storage volume by 50%)
Both systems, percolation or wet detention, require a baffle, 4"-6" minimum below the low water level and up to the high water level, unless your contributing area is at least 50% green.
If a wetland is available for treatment, then the first 1/4" of runoff must be intercepted outside the wetland in a 6" deep swale or a baffled sediment sump must be used.
Conclusion, ask the regulators what your local requirements are!!
Clifford H Laubstein
FL PE 58662