SprinklerDesigner2
I have a two story bank building.
The first two floors are non-combustible construction with metal studs, masonry and drywall.
The attic is wood truss and will need to have a dry system protecting the space.
The architectural drawings shows batt insulation between the bottom chords of the truss. It appears the bottom of the wood trusses will be exposed.
Here's a screen capture.
My question is will the space between the bottom of the wood truss and second floor suspended ceiling need sprinklers?
From NFPA #13 - 2002
8.14.1.2.13 Concealed spaces below insulation that is laid directly on top of or within the ceiling joists in an otherwise sprinklered attic shall not require sprinkler protection.
I think this applies, the space doesn't need sprinklers but I would feel better with confirmation.